Settings of Boss823's 28kW S4
There are 22 replies in this Thread which was already clicked 11,248 times. The last Post () by mare.
  • 15kw and 22kw are the same,Just Ventilator on 15kw is limited to 85%. 22kw and 28kw have ventilator set to 95%, but 22 have 190C set point 28kw have 210Cset point. Betwen 22 and 28 is diffrience in wider turbolators.
    Very thanks to this information.
    Which model has the wider turbolators? 22 or 28 kw?
    How can I change on my froling 28 kw set point gas temperature from 210C to 200C or 190C?
    I have a froling s4 28kw with 1800l puffer + 300l boiler.
    This is my kessel:
    http://lucabrt.url.ph/status.html
    Thanks to Bashy of this forum!
    Thank you
  • Go into the service mode (code is -7), there you can change maximal and usual ex. gas temp.
    Thanks Reichl!!!
    I just tried to set it from 200 C to 190 C. In your opinion It is better 190 or 200C?
    Which is your tem. setting?
    this is my froling system:
    http://www.lucabrt.url.ph/status.html
    If you click on "allinonestat" you can see that "vorlauf 1" detects always 127 C° also if the kessel is running and also if the kessel is off and its temperature is 30 C°.
    What is "vorlauf 1" ?? and why it detects always 127 C ??
    I have just looked into service menu and i discover this value (see image)
    "flue gas temperature after the condenser" that It is 127 C.
    what it is???
    and how is possible 127 c If the kessel is cold?
    It's an error?
  • And about settings....
    My ventialtor is set to 95% (it works always on 95% for all the time, for only some minutes the fan goes down to 90-93% is it normal?.)
    Lambda is set to 8%
    I would like to try this settings for my froling s4 28 kw:
    Max gas temperature 235
    Set Gas temperature 190
    Fan ventilator : 93%
    Lambda: 8%
    What do you think?
    Thank you
  • 127°C means, that a sensor is not connected.
    If you don't have a flue gas condenser (I am quite sure you don't have one), just ignore it.
    Please read your user manual.
    Be careful in the service menu, you can render your S4 unusable.
    Please talk with your hydraulico and your local Froeling service guy and understand your setup before changing parameters.
    thanks for reply!
    My hydraulico froling settings was:
    Max gas temperature 250
    Set Gas temperature 200
    Max Fan ventilator : 95%
    Lambda: 8%
    Yesterday I changed It in:
    Lambda: 7,6%
    What do you think?
    Can you post yours settings please?
  • You can not copy settings from another user to your oven. They depend on chimney, wood and local hydraulics.
    I have got an S4/15kW and just lowered the exhaust temp to 190°C.
    Watch your combustion, ash and inside walls.
    Generated own thread for you.
    Looked at your graphics, looks ok. Which kind of wood you burn?
  • The percentage of heating power? .....What does it means?
    On my s4 28kw, it would say that if kesselstrg is 100% the kessel is heating for = 28 kw ?
    And if it is 50 % the kessel is heating for 14 kw?
    It is in this way?
  • ...But I'm not sure about this.....
    Look at the photo below just done:
    Now kessel is cold but kesselstr is always 100%. ...and the kessel sure don't run 28kw now because it is off :)
    Another thing:
    Which is the difference between AGT vs AGS temperature?
    Thanks
  • When off it is always 100%, really!
    .....sorry but I don't understand......
    It is 100% also when it is off. Is it normal? ( i don't understand this, if you can explain me please)
    AGS is Soll temp (should be)
    AGT is Real temp.
    Do you have an operators manual?
    What does it means "soll" ?
  • deriva dal verbo "dovere". è la temperatura che prova a ottenere in questo momento. Non è importante! KST dovrebbe essere sempre 100%; vuol dire piu o meno potenza ottima
  • What do you think about my graphic?
    [Blocked Image: http://www.webalice.it/boss823/232.jpg]
    It is working with this setting:
    Max gas temperature= 235° (original it was 250)
    Set gas temperature= 186° (original it was 200)
    Lambda= 7,6% (original it was 8%)
    What do you think about?
    any advice?
    I noted that "kesselstrong" in the middle of the graphic is low (70-80%) ; It is ok or not?
    ps. all others setting are default original by froling
    Thanks